Reluctant pool guy Posted July 17, 2021 Report Share Posted July 17, 2021 Putting in inground pool. Pump comes factory wired for 230v. Installed 2 SqD Homeline GFCI 20amp breakers w/#10 wire to a 2-pole commercial grade switch to turn motor off/on. Breakers trip immediately when trying to “bump” motor. Also uncertain if my son didn’t get windings of motor wet being overzealous w/hose washing concrete. Should I dry motor w/het gun/blow dryer? Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 17, 2021 Report Share Posted July 17, 2021 GFCI Wired wrong would be my guess Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 17, 2021 Report Share Posted July 17, 2021 9 hours ago, Reluctant pool guy said: 2 SqD Homeline GFCI 20amp breakers You cannot use 2 120v gfci breakers to feed a 240v pump. Get a 240v gfci breaker. 2 Quote Link to comment Share on other sites More sharing options...
cranbiz Posted July 19, 2021 Report Share Posted July 19, 2021 You need one of these. https://www.amazon.com/Square-Schneider-Electric-HOM220GFIC-Homeline/dp/B00L40PKFK/ref=sr_1_2?crid=5VTND25BKVW9&dchild=1&keywords=homeline+20+amp+240+volt+gfci+breaker&qid=1626705824&sprefix=Homeline+20amp+240%2Caps%2C174&sr=8-2 Quote Link to comment Share on other sites More sharing options...