We are had the electrical redone for a new tub, our electrician was given the specs and the instructions.

We just learned he used 6 wire instead of 8 on our hot spot tempo, we were told it wouldn't meet code using the 8 wire on a 50 amp circuit. Am I going to have issues?

The tub is connected and it's filled I just started balancing the water. Any input would be appreciated!

Link to comment
Share on other sites

The #6 is difficult to fit into the spring clamp terminal block of the Hot Spot control box. You may want to ask the electrician if he can put a #8 pigtail at the end. The # 6 can carry a larger load, but it has a problem with that control box... it doesn't make good contact in the terminal block- the small internal springs in the terminal block cannot be tightened, they're just spring loaded. The #6 is pretty rigid, not pliable, and the little spring clamps have a tough time accommodating it, and holding it securely. They have no issues with #8

Link to comment
Share on other sites

What TYPE of conductor did the electrician use?? If he used something like UF, it was probably temperature rated at 60C which would only give the #8 a 40 amp rating. If he followed Watkins requirement to use 75C or higher conductors ( such as THWN, THHN or THWN-2), that #8 would have a max ampacity of 50 amps at 75C or 55 amps at 90C, as referenced in the Tables included in Article 310.15 of the NEC. As usual, the engineers at Watkins are correct and your electrician and/or inspector are the idiots.

John

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...