Spa continues to over flow into pool despite spa mode with valves properly set


Recommended Posts

As the title says, my spa continues to overflow into my pool, even in spa mode. 

The valves are properly set, with the actuator-contolled spa drain open and the  actuator-controlled spa return open. 

This is the exact setup that worked correctly until a few days ago, when I had a new heater installed. No valve settings were changed when the heater was installed.

Any ideas why the spa continues to overflow?

Thanks.

Link to comment
Share on other sites

Several things can cause this. Since the spa continues to overflow in spa mode it means the spa drain line is not opening. This could be from a defective valve or actuator, actuator out of sync or adjustment. or a defective or stuck check valve. Diverters and check valves do wear out (which is why the major manufactures sell repair kits for their valves). It is possible that something got damaged or something got stuck in the valve or diverter when the heater was installed. I would contact the company that installed the heater and tell them that you are having plumbing problems since the installation. They might find that they are responsible or they might find that your valve, actuator, or diverter needs to be repaired or replaced (which means you will have to pay).

Link to comment
Share on other sites

Not necessarily. Actuators are not always set to completely open or close a valve. For example, they could be set to only partially open the spa valve to allow both spillover and pool returns (very common if it is desired to run the spillover when the pool only mode is in operation) and same with the drain lines to allow the pool skimmer or drain to also operate in spillover mode If yours are only opening or closing partway it would explain this. I would assume that your setup uses a shared filter and pump for both pool and spa since this is the normal way a spillover spa is plumbed.

 

Link to comment
Share on other sites

7 hours ago, KJIsaacson said:

FWIW, I leave the spa drain valve open when the pool is off, the spa drains into the pool.

Do you mean that you empty the spa into the pool when the pool is off or that the spillover is active when the pool is off? Does your spillover operate in pool only mode or do you need to set it to spillover mode. What is the brand and model of your automation system?

Link to comment
Share on other sites

Waterbear, first I want to thank you for your help and the attention you're giving to my issue.

I'll clarify one thing that I did by way of typo in my FWIW remark. I meant to say IF ieave the spa drain valve open when the pool is off, the spa drains into the pool. That is not my practice. It was simply a way to check whether the valve was actually opening the spa drain. It does. If the pump is off, and I open the spa drain, the spa drains, and it does so rather quickly.

To answer your other questions:

Normal pool operation:

  • When in pool mode:
    • Water leaves the pool through the pool drain and the skimmer (as shown in the accompanying picture. The inlet labeled "To spa jets" is closed while in pool mode. NOTE: the diverter valve that controls the spa drain is usually a valve actuator. It "went" a few days ago, and I'm replacing it. Normally, it would automatically rotate 180 degrees from the position shown in the picture when switched from pool mode to spa mode. Right now, I'm doing that manually.
    • Water comes into the spa by way of a single inlet, labeled "To spa overflow". Water also enters the pool by way of floor pop ups (labeled in picture). The result: Water overflows the spa into the pool, as desired.
  • When in spa mode:
    • Water leaves the spa because the spa drain is now open. Water continues to leave the pool through the pool drain and skimmer. (I can manually shut either the pool drain or the skimmer, but not both. This has been the case for years. It stays in the position show (taking water in from both pool drain and skimmer, while in either pool mode or spa mode.)
    • Water comes into the spa by way of spa jets (labeled). No more "in" through spa overflow or floor pop ups.

As for the brand/model of the automation, all is controlled by a Waterways Plastics Oasis Pool and Spa control. The actuator valves are Hayward GVA24. There are two actuators. One that opens/closes the spa jets or spa overflow/pool floor pop ups (as shown), and the other that opens/closes the spa drain (controlled manually right now, but to be replaced).

As previously stated, all was working well, with these same valve settings, until a few days ago. I can confirm that the valve controlling the spa drain is indeed working. I manually turn it, and I can hear the water flow changing. Similarly, the valve controlling the spa jets into the into the spa is working. 

I'm stumped and would appreciate any further thoughts you might have!

Thanks again.

 

08-07-23 - In.jpg

08-07-23 - Out.jpg

Link to comment
Share on other sites

Imagine my embarrassment! I just discovered my own mistake, and I'm so sorry to have wasted your time. 

I just found that when I switch to spa mode, I can and should  close off the pool drain and skimmer as I open the spa drain. This, of course, causes more water to be drawn from the spa and eliminates the overflow from the spa into the pool.

My mistake was rotating the spa drain diverter valve a full 180 degrees instead of just 90 degrees. The previous actuator was obviously set for the proper 90 degree rotation, and I'll be sure to set the new one that way.

Again, thanks for your help and sorry for wasting your time!

Best.

Link to comment
Share on other sites

1 hour ago, KJIsaacson said:

Imagine my embarrassment! I just discovered my own mistake, and I'm so sorry to have wasted your time. 

Not a problem, I bet that if we hadn't interacted  you would not have realized that the spa valve should only be turned 90 deg and not 180.

 

11 hours ago, waterbear said:

Actuators are not always set to completely open or close a valve.

Bet that got you thinking about how your setup works.

It's all good and I'm glad that you got it worked out!

Link to comment
Share on other sites

16 hours ago, waterbear said:

Not a problem, I bet that if we hadn't interacted  you would not have realized that the spa valve should only be turned 90 deg and not 180.

Bet that got you thinking about how your setup works.

It's all good and I'm glad that you got it worked out!

Indeed. Thanks again. 

In addition, the reading and video watching I did before installing the actuator helped immensely. I had the cams set perfectly before the install, and it worked as desired as soon as I powered up.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...