nealcook Posted September 4, 2014 Report Share Posted September 4, 2014 Pentair EasyTouch system will not hold temp calibration. I followed the instructions, place in service mode, changed the temp to the correct temp (increase of 4 degrees), press menu to set and return to auto mode but the changed setting is not saved. Any ideas on how to make the system save the new setting? Quote Link to comment Share on other sites More sharing options...
MikeThePoolman Posted October 1, 2014 Report Share Posted October 1, 2014 I've been in the same situation. At this point i would replace the temp sensor. Its either the sensor or teh board. Pray its the sensor Sincerely, Mike the Poolman Quote Link to comment Share on other sites More sharing options...
Pool Clown Posted October 3, 2014 Report Share Posted October 3, 2014 System not holding temp calibration MAY not be the sensor. Try switching your freeze sensor to the water sensor position (small screwdriver needed). This will verify that it is, or is not the sensor. Quote Link to comment Share on other sites More sharing options...