Hi everyone,

I'm pretty baffled by this hot tub issue so I wanted to see if I could get some help. I tried to be as descriptive as possible.

I'm renting a home and a (broken) hot tub came with it - it is a 1989 Coleman Horizon 211 wired at 240v. The owner said I can do whatever I want to try to fix it, so I thought why not, I'll give it a shot. It hadn't gotten much use over the years and, with the mild climate in San Diego, the tub really seemed to be in good shape.

Turned it on, jets work fine, lights work fine, only problem is it won't heat. So I fiddled with it some and finally figured out the high-limit switch was pushed out. I pushed it back in and left it to heat with the cover on overnight, and when I checked it the next morning, it was steaming hot.

I thought great, I'll just drain it, clean it, fill it back up and I'll be good to go. After refilling the tub, the heater once again wouldn't heat (at all). The jets work fine with a constant stream, there were no air locks (that I could find), and I even took out the heater element and pressure switch and replaced them - no dice.

I checked the voltages of the heater components while it was running and everything seemed constant (across the heater element and across the pressure and high-limit switches). I haven't replaced the high-limit switch, but I did try bypassing it with no luck. I've tried adjusting and even bypassing the pressure switch, but still the water won't heat at all; it stays at 70 degrees. I also tried removing the filter altogether to improve flow, to no avail. When I turn the temp up on the control panel, the heater light does come on, and there is a single audible "click" sound from the main panel where the wiring is located, but I don't get any heating, and the heater's housing certainly never feels hot (even with the new heater installed). I did open up the main panel wiring, and it's quite a mess, but I didn't see anything blatantly disconnected or burnt. The two fuses I could find also seemed to be intact.

Any ideas what might be wrong? I know it's an old machine, but I'm having fun with the fix. I've also attached what I think is the user manual in case anyone is interested.

Thanks in advance!

-Steven

1988-1989-Coleman-Spa.pdf

Link to comment
Share on other sites

I have a 1988 CalSpa, your Coleman likely is somewhat different.  My heater element is a simple 5500 watt element like in a home water heater, and I've changed that every few years.

rheem-protech-water-heater-elements-sp10

If you get 240 volts across the heater terminals, that's good.  Did you also disconnect the wires (with power switched off, of course) and then measure the ohms resistance across the heater terminals?

Link to comment
Share on other sites

Hey Cusser - thanks for your response. This is my heating element (also 5500 watts):

bx5002-1500-A-490x490.jpg

 

Link is here.

Measured the ohms across the terminals at 10.7, but you're right - I'm only getting 0.5 volts across the terminals (and at the high-limit and pressure switches)! What could be causing this? A bad heater relay?

Link to comment
Share on other sites

It's the heater contactor.  If you google the part # they are available.  Check the wiring while you're in there.  Loose or corroded wiring can cause contactor failure but it looks to me that the contactor itself got corroded.  Did you hear any chattering or clicking before the heater failed?  Lots of information on the web on contactors.

Link to comment
Share on other sites

Thank you! I am reading up about them now. There was a good bit of clicking/chattering before it failed.

Last question for now, these are the ratings on the side of my broken contactor:

VAC           FLA    LRA      Non-ind

240-277     20      120

480             20      100       30 amps

600             20       80

If I buy a replacement like the one below, with higher ratings, should it still work?

https://www.amazon.com/Holdwell-45EG20AG-Definite-Purpose-Contactor/dp/B01J4Z8QQG/ref=sr_1_22?crid=1PCCNL86HJGOH&keywords=definite+purpose+controller&qid=1554603485&s=gateway&sprefix=community+coff%2Caps%2C176&sr=8-22

Link to comment
Share on other sites

not knowing what your setup is, one side of your contactor slants in on both sides.  I would make sure that there is room for the other one because the corners are squared off.

Can you google the actual part no?  I can't read it in the picture.  I also don't see a connector on both sides of the contactor in your picture.  The amazon part has it on both side another reason why it may not physically fit 

 

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...