Question About Adding Gfci Subpanel To Older Jacuzzi...


Recommended Posts

I have an older Jacuzzi hot tub installed before GFCI was required. I'd like to upgrade to GFCI, but I have a Zinsco panel (It's in great shape) and I am unable to locate a zinsco 60 amp breaker with GFCI.... which leads me to a subpanel.

The jacuzzi is 240v only with 2 hots and an insulated ground run through RMC about 40' from the panel. My thought was to simply cut into the RMC about 20' away from the tub and install the GFCI panel, but all the GFCI's I've seen have a neutral pigtail, but the wires in the RMC don't include a neutral, only a ground. To further muddy the water, on a Zinsco main panel all the grounds terminate on the neutral bar. Do I just not use the pigtail or does the pigtail go to the insulated ground wire in this case as if it were a neutral?

Link to comment
Share on other sites

In the MAIN panel, the grounding bar and neutral bar are one and the same. In subpanels they're separate

There are GFCI 240v breaker without the neutral pigtail....a bit harder to find (try an electrical supply house rather than a hardware or big box store), they're also less $.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...