Redundant Gfci Protection


Wobbly

Recommended Posts

Last year I installed a subpanel with a GFCI feeding the hot tub. The hot tub already had another GFCI in the control package. Recently the subpanel GFCI has tripped out. Inspecting the control package, it looks like the GFCI in the control package is damaged. The trip button seems to be a bit distorted and seems to be stuck.

The control pack is 15 years old. I've replaced a few relays and a heater element in the past.

I thinking about removing the control pack GFCI to see if that will stop the subpanel GFCI from tripping.

The last time there was GFCI tripping was due to a slight water drip onto the top of the control pack. After it was dried out the problem went away. This time, drying the pack didn't seem to help.

So is there any danger from removing the control pack GFCI?

Link to comment
Share on other sites

Last year I installed a subpanel with a GFCI feeding the hot tub. The hot tub already had another GFCI in the control package. Recently the subpanel GFCI has tripped out. Inspecting the control package, it looks like the GFCI in the control package is damaged. The trip button seems to be a bit distorted and seems to be stuck.

The control pack is 15 years old. I've replaced a few relays and a heater element in the past.

I thinking about removing the control pack GFCI to see if that will stop the subpanel GFCI from tripping.

The last time there was GFCI tripping was due to a slight water drip onto the top of the control pack. After it was dried out the problem went away. This time, drying the pack didn't seem to help.

So is there any danger from removing the control pack GFCI?

As long as the system is connected properly to a GFCI breaker, the pack GFCI can be bypassed.

Link to comment
Share on other sites

Last year I installed a subpanel with a GFCI feeding the hot tub. The hot tub already had another GFCI in the control package. Recently the subpanel GFCI has tripped out. Inspecting the control package, it looks like the GFCI in the control package is damaged. The trip button seems to be a bit distorted and seems to be stuck.

The control pack is 15 years old. I've replaced a few relays and a heater element in the past.

I thinking about removing the control pack GFCI to see if that will stop the subpanel GFCI from tripping.

The last time there was GFCI tripping was due to a slight water drip onto the top of the control pack. After it was dried out the problem went away. This time, drying the pack didn't seem to help.

So is there any danger from removing the control pack GFCI?

As long as the system is connected properly to a GFCI breaker, the pack GFCI can be bypassed.

The spa pack GFCI was removed and now the hot tub is running. Thanks.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...