A 200 amp box will feed lots of circuits - so I assume you have a large house.

Can you double up one other circuit with a 'buddy beaker?' That is a breaker which fits two circuits into the space normally occupied by just one breaker. It will not run your spa, however, it would give room for a two-pole 50A breaker, which is most likely what you do need for your spa. Here's a picture of a 'buddy breaker' or double half-wide breaker.

QOT1515%20Circuit%20Breaker_lres.jpg

Or put a sub panel next to the main and move a breaker or two to that.

B)

Link to comment
Share on other sites

If it were me depending on how long you plan on staying at the house, i would take this opportunity to add a 100 amp subpanel nearby or closer to the tub, in lieu of the buddy breakers. You will likely only need to ad more breakers down the road anyway, if you are full now. You can get a murray 100amp subpanel package at the chepot with breakers pretty reasonble. you will need to relocate some of the circuits to the new panel to accomodate the panel breaker.

Link to comment
Share on other sites

Unless you're adding a new "service", a subpanel is only going to give you more room, not more amps. A 125A subpanel connected to a 200A main panel isn't going to give you 325A, you'll still only have 200A. Now, I do agree that a subpanel is the cleanest and safest way to do what you want to do, but if this is more about amps than space you need to have your service upgraded.

Link to comment
Share on other sites

First thing I wouldn't have a "handyman" do real electrical work. Hire a real electrician. If you do that you don't need to worry about much more. Here's the things to look at. How many amps is your service? If smaller, say 100amps: Do you heat with electric or gas? What's the max load on your service at any given time? I really doubt that you would overload even a 100amp service in the dead of winter even if your heating with electricity but still things to take into account. As far as the breakers go. You can mini up some of them and create room. Just need to be aware of multiwire circuits and keep your phasing correct.

Link to comment
Share on other sites

We ran into the same situation. We had one slot open at the bottom of our panel, but needed two. We had an outlet in the garage that was dedicated for a chest freezer. Since we haven't had a freezer out there in years, we just did away with it and moved something up to it's place, which freed up a much needed space at the bottom.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...