Not just possibly, it is certainly custom. From what I can see the installer worked cleanly but I'm not as sure about how close to code he worked.
There are two relays, a 110 to 12/24 stepdown transformer, a 4 amp circuit breaker and 110v outlet into which is plugged a remote control receiver.
I can't see the specifics of the wiring and I'm not certain of the function of the two relays but this is what I would do:
- Check for 110 at the outlet, correct if missing then
- Check for the remote receiver functioning by measuring voltage across the two output screw terminals. Voltage should be present when off, and zero when on. If no voltage in either state check it again by removing one of the wires and check for resistance when switched on and off. When remote on resistance should be near zero, when remote off it should be infinite. fix it it it's bad. Then
- Check the input of the transformer with the remote on. It should be getting 110v, possibly also when the remote is off. I can't say anything else from here because the photo is not detailed enough to tell, and I'm not certain what the relays do.
From the look of the box I'd say it has some years on it and a bit of weathering but it also looks like a weather-tight enclosure so the weathering shouldn't be too much a problem.
Thanks for the detailed reply. Now what would require a 12/24v supply? The heater?
Edit: I think I answered my own question - it's the underwater pool lights.