Just now, Reese62 said:
Cold weather and electricity was going off and on very often for about 3-4 hours before I thought to turn off breaker to spa. Once outages quit happening is when I tried to turn it back on and the breaker started tripping.
Guess I will start unplugging different circuits tomorrow and find what is tripping breaker.
-
2 hours ago, RDspaguy said:
Oh, I just noticed the "surge" post. Please explain.
-
2 minutes ago, Reese62 said:
Most of the time it trips immediately. The last time I shut off main breaker and left off for 30 minutes to let any internal resets to reset if there are any. When I turn the 30 amp back on, it took about 5 secs to trip.
Hot springs pulse. 2016
-
1 hour ago, castletonia said:
I assume you have either a Hot Spring or Caldera hot tub with dual breakers 20A/30A. If so, which model and how old? Does the 30A trip instantly when you reset it and if not, how long does it take to trip?
Most of the time it trips immediately. The last time I shut off main breaker and left off for 30 minutes to let any internal resets to reset if there are any. When I turn the 30 amp back on, it took about 5 secs to trip.
-
Power outage / surges
30 amp breaker keeps tripping after several power surges or outages
in Portable Hot Tubs & Spas
Posted
Nothing extra added. So no ozone