heytat Posted January 29 Report Share Posted January 29 I have a 2009 hot springs jet setter with a problem I can’t diagnose. It is wired up in a 220V configuration and has worked generally ok for a long time Every now and then it will pop the 20A breaker about 5-10 minutes into running the jets. When this happens there is a short burst of very hot water that comes up from the bubbler on the floor of the tub. When I reset the breaker everything is ok for hours or days. Any thoughts? Quote Link to comment Share on other sites More sharing options...
cranbiz Posted January 30 Report Share Posted January 30 The 20A breaker runs everything except the heater. Does the tub have an ozone generator? If so, try disconnecting that. The generator is only good for a few years and is likely not functioning correctly. 1 Quote Link to comment Share on other sites More sharing options...