Boo Posted February 8, 2022 Report Share Posted February 8, 2022 Just finished replacing legacy hardware. Upgraded to this VS 501z and Topside control panel. Programming question. Pump continues to run while in standard mode.. Seems to shut down in in Economy mode. Only Dip switches I have set are 3 and 10. It keeps temperature well.. Runs Great.. Yes It has an insulated cover. All I did was retrofit the hot tub for new hardware, I figure its probably an easy fix to someone more knowledgeable. One motor, Prozone, New VS501z and jets.. Nothing special. Actually pump just kicked off. So I guess its working correctly. Lol... The Template I'm not using seems to be the one I need to use since I don't have a blower. Guess that would require reprogramming something to make the buttons designated.. When I use the Balboa, Blower kicks the pump on low. Guess that's normal. Should I leave it alone considering all other buttons work as they should? Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted February 8, 2022 Report Share Posted February 8, 2022 In standard mode it will run pump 1 low speed any time it needs heat, plus filter cycles. Economy means it only starts the pump for the filter cycle, not if it calls for heat, but will continue to run it beyond the filter cycle until it reaches set temp. 1 Quote Link to comment Share on other sites More sharing options...