2 hours ago, RDspaguy said:

Unplug the main pump and see if it stops tripping and starts heating.

Chinese made LX pump and they have been VERY reliable from my experience however they are prone to breaker trips when they do fail. Use advice posted by @RDspaguy Let us know results

Link to comment
Share on other sites

So I rechecked amperage today when it tripped. It hit .6. Only the circ pump running 

 

The heater ohms at 12 when checked. 
 

for fun I took the old heater element and tested it for short. It read 0 when checked but there was a spot on the element that was abraided and when I put probes there the meter read 5 and change. 
 

im beginning to think it’s the heater. 

C6F5B5F9-7550-4F68-85AC-C8DFC04946D9.jpeg

Link to comment
Share on other sites

It trips even when the pump is unplugged? 
- yes, I can run it all day long with circ pump, pump 1(cheap Chinese pump) and light plugged in as long at the heater is not connected. Once you connect the heater it trips in plus /minus 24 seconds and only shows .6 amp draw (with pump 1 unplugged). 
 

if it warms up tomorrow, I may swap out heating elements with one of my old ones. 

Link to comment
Share on other sites

 

Sounds like to board is good and the issue is either in the heater element or the GFCI. When you installed the element did you ensure it was not touching the side walls of the heater tube?
 

- I actually replaced the unit as a whole (control pack/heater factory mounted) unit so I didn’t even think to check it before mounting. I have two older heat elements in my parts pile. One checks out when I put the ohm meter on it. I am going to try and swap the elements/heat tube out today if I can get a minute. Crossing fingers that this works. I really don’t think it’s the breaker now after seeing .60 amps on the clamp meter. 

Link to comment
Share on other sites

A faulty gfci can trip regardless of load. A gfci breaker is 2 things, a breaker, which regulates amp draw, and a gfci, which protects from ground faults (the loss of voltage to ground as occurs in most electrocution deaths). Either component of the gfci breaker can fail.

If the heater has a fault, you can find it with an ohm meter. Disconnect heater and test for continuity (ohms) from either heater lead to the heater ground or metal housing. Continuity, or any ohm reading other than infinity, is a bad heater.

 

  • Like 1
Link to comment
Share on other sites

18 hours ago, RDspaguy said:

A faulty gfci can trip regardless of load. A gfci breaker is 2 things, a breaker, which regulates amp draw, and a gfci, which protects from ground faults (the loss of voltage to ground as occurs in most electrocution deaths). Either component of the gfci breaker can fail.

If the heater has a fault, you can find it with an ohm meter. Disconnect heater and test for continuity (ohms) from either heater lead to the heater ground or metal housing. Continuity, or any ohm reading other than infinity, is a bad heater.

 

One of my old elements when tested with a probe on a terminal( element removed from tube housing) and the other probe to the element reads 0.00 when multi locations are checked. I did find one place where I touch the element and get an ohm reading of 5 and change. 
 

if put the element in the tube and check one terminal and the exterior of the tube it reads 0.00. Is this a good or bad element?

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...


×
×
  • Create New...