jamesey Posted July 7, 2020 Report Share Posted July 7, 2020 I tried opening my hot tub for the season. I filled it with water. Turned the breaker on and pump 1 didn't come on. Pump 2 worked fine. Tried removing the filter and it made no difference. The 25 amp fuse was blown. After the fuse was replaced. I turned the breaker back on and it immediately turned off at the panel and popped the new fuse. No idea what changed, but now the breaker won't stay on with a bad fuse in it. Have to remove pump1 wire from spa panel. Maybe when the fuse completed the circuit again it made the short worse after the next pop not sure. Tested 1 component at a time and if everything was plugged in with pump 1 being unplugged. I could turn the breaker on and it would be fine. This made me think pump 1 was bad. I turned off the breaker, plugged pump 1 back in, pump2, heater, etc and unplugged both the flow switch wire and the HI temp wire coming from the heater at the spa panel. Turned the breaker on and it the breaker didn't pop. Now I am thinking pump 1 is fine and the heater is bad. The main power plug from the heater to the panel does not trip the breaker. It only trips when pump 1 and heater is plugged in and both the flow switch and temp sensor is plugged into the spa panel. I think it's strange that the temp sensor or the flow switch would trip the breaker, but the main power plug for it does not. Has anyone experienced this? How can I be absolutely sure it's the heater before spending $160 to get a new one? Other details arctic spa Klondiker made in 2007 . Heater closely resembles Thermcore heater C2550-0103TT Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 7, 2020 Report Share Posted July 7, 2020 Flow switch protects the heater. If there is no or low flow it won't allow the heater to fire. When you start up the pump 1 should start first and then the flow switch detects the flow and starts the heater. If the heater is bad it will trip the breaker at this point. Have you disconnected just the heater from the circuit board and tried to start it without the heater connected? The fuse green buss fuse (SC 25) protects the pump so is you have the heater disconnected and the pump fuse blows you have a pump short. What fuse is blowing? Please post photos of your circuit board 2 Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 7, 2020 Author Report Share Posted July 7, 2020 @CanadianSpaTech, 47 minutes ago, CanadianSpaTech said: Flow switch protects the heater. If there is no or low flow it won't allow the heater to fire. When you start up the pump 1 should start first and then the flow switch detects the flow and starts the heater. If the heater is bad it will trip the breaker at this point. Have you disconnected just the heater from the circuit board and tried to start it without the heater connected? The fuse green buss fuse (SC 25) protects the pump so is you have the heater disconnected and the pump fuse blows you have a pump short. What fuse is blowing? Please post photos of your circuit board Hi CanadianSpaTech, Thank you very much for your response. If I turn it on with the without the heater connected (main wire), but leave the other 2 HI temp & Flow and pump 1 is plugged in (with good or blown fuse) it will pop the circuit breaker. It's the pump 1 fuse that blows SC-25. I don't think it's the pump with the short since it can be plugged in providing the FLOW & Hi Temp are not connected. I ordered a new fuse and will try to see if I can get pump 1 to run while FLO switch & HI Temp wires are disconnected. That was my next plan of attack. I am sorry, but I do not have a photo of the panel at this time. I will take a picture next time I open up the cabinet. When the fuse comes. Didn't want to leave it open because of rain and animals. Could I use a multimeter to determine if the heater is causing the short? If so, what is the process for that? Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 14, 2020 Author Report Share Posted July 14, 2020 On 7/7/2020 at 12:09 PM, jamesey said: @CanadianSpaTech, Hi CanadianSpaTech, Thank you very much for your response. If I turn it on with the without the heater connected (main wire), but leave the other 2 HI temp & Flow and pump 1 is plugged in (with good or blown fuse) it will pop the circuit breaker. It's the pump 1 fuse that blows SC-25. I don't think it's the pump with the short since it can be plugged in providing the FLOW & Hi Temp are not connected. I ordered a new fuse and will try to see if I can get pump 1 to run while FLO switch & HI Temp wires are disconnected. That was my next plan of attack. I am sorry, but I do not have a photo of the panel at this time. I will take a picture next time I open up the cabinet. When the fuse comes. Didn't want to leave it open because of rain and animals. Could I use a multimeter to determine if the heater is causing the short? If so, what is the process for that? @CanadianSpaTech, Here is a photo of the panel. I plugged in pump1, replaced the pump1 fuse and it blew again as soon as I turned on the breaker. Which also popped. I had the hi temp and Flo switch disconnected, but the main heater wire plugged in. I am back to thinking it's the pump and not the heater. I spoke to waterway to see what pump would replace the yellow one pictured and they recommended Model: 3721621-1D. Please let me know what you think. Thank you!! Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 14, 2020 Author Report Share Posted July 14, 2020 On 7/7/2020 at 11:08 AM, CanadianSpaTech said: Flow switch protects the heater. If there is no or low flow it won't allow the heater to fire. When you start up the pump 1 should start first and then the flow switch detects the flow and starts the heater. If the heater is bad it will trip the breaker at this point. Have you disconnected just the heater from the circuit board and tried to start it without the heater connected? The fuse green buss fuse (SC 25) protects the pump so is you have the heater disconnected and the pump fuse blows you have a pump short. What fuse is blowing? Please post photos of your circuit board Photos posed below in thread. Sorry I think I put it in the wrong spot. Newb Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 14, 2020 Report Share Posted July 14, 2020 No that is not the right pump do not order. Arctic Spa and those yellow pumps are usually 2.5"" inlet and a 2" outlet. Look at the pump wet end and if you notice the one with the red plumbing at the face of the pump will be a larger pump union than the one coming off the side of the pump with the withe plumbing. Those Yellow pumps often fail and trip the breaker. European made and tough to get parts for. Best to replace with a Waterway. Waterway 2.5" x 2" Part number: WW 3721621-13. If you are unsure of size post a pic of the wet end so we can see both pump unions. 1 1 Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 15, 2020 Author Report Share Posted July 15, 2020 22 hours ago, CanadianSpaTech said: No that is not the right pump do not order. Arctic Spa and those yellow pumps are usually 2.5"" inlet and a 2" outlet. Look at the pump wet end and if you notice the one with the red plumbing at the face of the pump will be a larger pump union than the one coming off the side of the pump with the withe plumbing. Those Yellow pumps often fail and trip the breaker. European made and tough to get parts for. Best to replace with a Waterway. Waterway 2.5" x 2" Part number: WW 3721621-13. If you are unsure of size post a pic of the wet end so we can see both pump unions. @CanadianSpaTech Thank you so much. you saved me! You are right it's 2.5 and 2". Can I use the cord/molded plug from the yellow one or do I need to buy one that goes with the waterway pump? I want to buy it from amazon for hassle free return just in case. They don't sell the one I need at the moment. I will keep checking as they sell every other one. Any chance I can use the 5 HP below or will I break something? Specs below in 2 screen shots. It's more HP and 3.5 amp higher speed (yellow one 12.9). No idea why they are selling it for the same price as the 4HP ones they have listed. Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 15, 2020 Report Share Posted July 15, 2020 3 hours ago, jamesey said: Can I use the cord/molded plug from the yellow one or do I need to buy one that goes with the waterway pump? Not 100% sure. I know that the yellow pump wiring is colour coded differently and the wiring connectors would have to be re-done. As for the 5 HP you would have to do the math on all the amperage draws of everything in the spa... both pumps, heater, ozone, lights ect to make sure you stay under the GFCI breaker rating if everything was running at once. Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 15, 2020 Report Share Posted July 15, 2020 3 hours ago, jamesey said: @CanadianSpaTech Thank you so much. you saved me! Just another day at the office 2 Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 15, 2020 Author Report Share Posted July 15, 2020 1 hour ago, CanadianSpaTech said: Not 100% sure. I know that the yellow pump wiring is colour coded differently and the wiring connectors would have to be re-done. As for the 5 HP you would have to do the math on all the amperage draws of everything in the spa... both pumps, heater, ozone, lights ect to make sure you stay under the GFCI breaker rating if everything was running at once. @CanadianSpaTech Thank you again!! My sub panel is 50amp. My spa doesn’t have the ozonator option (2008). It was an option at the time that I didn’t purchase. 2-speed pump 1, single speed pump 2, heater, lights, aqua tremor speaker. The manual states my model equipped with 4 pumps needs a 60amp panel. Since I only have 2 pumps does that mean I should be fine moving up to the 5hp model For pump1. Yellow 4hp was 12.9 the 5hp one is 16.4. Pics of panel and specs are attached: Thank you thank you thank you Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 15, 2020 Report Share Posted July 15, 2020 16.4 + 12.9 (pump 2) both on high...call it 30 amps 5.5 KW heater= 24 amp plus stereo and lights A lot of systems will cut out the heater when both pumps are on high Can't remember if the Gecko MSPA pack does or not @RDspaguy Thoughts Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 16, 2020 Author Report Share Posted July 16, 2020 (edited) 1 hour ago, CanadianSpaTech said: 16.4 + 12.9 (pump 2) both on high...call it 30 amps 5.5 KW heater= 24 amp plus stereo and lights A lot of systems will cut out the heater when both pumps are on high Can't remember if the Gecko MSPA pack does or not @RDspaguy Thoughts @CanadianSpaTech I think I found what you are talking about. LC/HC jumper setting? If the jumper is on HC maybe I should move it to LC? I’m speculating it’s high current mode / low current mode. Low would cut out heat when both pumps on high? pic attached of inside spa panel diagram. Added another pic which I think is the jumper that appears to be in LC mode. -edit I was looking at jumper 2. I can’t tell from pic if jumper 1 is in LC or HC mode. after reading the below I am wondering why it’s set to LC mode. Should I move it to HC? -edit never mind. Didn’t realize it says more than 2. I should leave it at LC and amperage will be fine. I hope ”Jumper 1 Current limiting option Jumper 1 is used to limit the current drawn when more than 1 pump (or a pump and blower) are activated at the same time. Position 1 = HC (High Current) mode Heater will be turned off if more than 2 pumps are on at high speed. Position 2 = LC (Low Current) mode The heater may not be turned on if any pump (1, 2 or 3) is on at high speed. The "Heater" indicator will flash to indicate a request for heat, but the heater will not be allowed to start.” -source Edited July 16, 2020 by jamesey Was looking at wrong jumper Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 16, 2020 Report Share Posted July 16, 2020 A pump is sized based upon the calculated head of the plumbing involved. Raising the hp of a pump can cause problems in both the plumbing and the pump motor. I would not recommend it. Low current mode should turn off the heater with both pumps on. 2 Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 16, 2020 Report Share Posted July 16, 2020 There you go. Get the right pump and no issues to worry about. 1 Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 16, 2020 Author Report Share Posted July 16, 2020 Thanks @CanadianSpaTech and @RDspaguy If I understand correctly. It's recommended to put the jumper 1 in LC mode? That will ensure the heater doesn't run when both pumps are on high. While waiting for your responses I read a few blogs (parts companies) that said it was ok to modest pump upgrades. Can't go from a 1.5hp to a 4hp, but a 3 to 4 was ok. Since 4 to 5HP is less of a jump percentage wise than the examples given I thought it would be ok. I also read other blogs in the past that said don't push the spa limits as the parts wasn't designed for the higher HP. Which aligns with your feedback. Knowing that this was my only option sold by amazon and only having one left in stock I pulled the trigger last night on the order. You see my neighbor bought a pool and my kids keep salivating out the window (pic enclosed). During the covid-19 pandemic we don't even visit family (who have pools). We are sheltered at the moment. This elevated my impatience. This morning I read your responses and I immediately went to cancel my order since it hadn't shipped yet. Realizing the blogs came from part suppliers who make money when things break! Wouldn't you know amazon had no issues canceling the secondary items in the order, but nope not the pump(pic enclosed)! So then I had a pump coming without fuses or cover lol. I quickly reordered them since the pump couldn't be canceled. I ordered the cover as my hard cover started letting water into the tub and I don't want to spend $400+ on a new walk-on cover at the moment. I figured it was a cheaper route for the moment! At this point I think you are both right, but I will take my chances. I refuse to take my kids to any pool during the pandemic and who knows if amazon will ever have my correct pump in stock any time soon. It's their return policy that keeps me from looking elsewhere. Quote Link to comment Share on other sites More sharing options...
CanadianSpaTech Posted July 16, 2020 Report Share Posted July 16, 2020 You'll be alright. My philosopy on pools is...never buy a house with a pool...buy a house next door to a house with a pool and be a good neighbour 😄 You could always upgrade the breaker to a 60 and then have the heater run when both pumps are on high. 1 1 Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 16, 2020 Report Share Posted July 16, 2020 I like your philosophy! If you change the breaker you must change the wire also. Wire size determines breaker size. The wire must be big enough to carry the amps or it could burn out or catch fire. 1 Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 17, 2020 Author Report Share Posted July 17, 2020 1 hour ago, RDspaguy said: I like your philosophy! If you change the breaker you must change the wire also. Wire size determines breaker size. The wire must be big enough to carry the amps or it could burn out or catch fire. I wasn’t planning on changing the breaker. It’s 50amp and spa manufacturer recommends 60amp panel when equipped with 4 pumps. I only have to. Thinking the LC mode will keep me well under the 50amps. The new pump 1 is 3.5 amps more on high speed than the one it’s replacing. I bought a new 25amp fuse to replace the fuse blown by the bad pump. Is there more to be concerned about? Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 17, 2020 Report Share Posted July 17, 2020 Aside from burning out your new pump or blowing apart glue fittings and jets, not a thing. Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 17, 2020 Author Report Share Posted July 17, 2020 17 hours ago, RDspaguy said: Aside from burning out your new pump or blowing apart glue fittings and jets, not a thing. @RDspaguyI meant on the electric portion already have jet covers falling off! Sounds like I need to get some glue. Do you really think the extra 3 amps & 1hp will destroy the arctic spa Klondiker? Have you heard of anyone going up 1 hp and destroying their spa? You know 1000x more about the spa's than I do. I only know enough to be dangerous and that wasn't by choice. Upset children was my motivation to get her back up and running! Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 17, 2020 Author Report Share Posted July 17, 2020 @RDspaguy@CanadianSpaTech I ended up reordering the wrong pump again, but this time on purpose. I also ordered this adapter https://www.spadepot.com/2-x-2-12-Pump-Thread-Adapter-wO-Ring-Gasket-P9326C719.aspx . Please tell me this was a good idea. It was suggested by waterway plastics. I will return the 5HP pump back to amazon. link to wrong pump. 2 inch wet end. current pump is 2.5 wet end and 2 to heater. At first I thought it would change the flow, but then I'm thinking what good is a 2.5 inlet if the output is constricted to 2 inch. So logically this made sense to me to just buy an adapter as suggested by manufacturer. https://www.amazon.com/gp/product/B004VTH8R4/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1 Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 18, 2020 Report Share Posted July 18, 2020 Adapter is fine. I have replaced pumps with a higher hp because that was what I had in the truck many times. Sometimes it's fine, but I have had valve caps, unions, and glue fittings blow out, and had a pump burn up in less than a year. I always warned my customers, but they often want it fixed immediately, so I use what I have but do not give a warranty. It's a gamble. Do you feel lucky? 1 Quote Link to comment Share on other sites More sharing options...
jamesey Posted July 27, 2020 Author Report Share Posted July 27, 2020 @CanadianSpaTech @RDspaguy Hi Guys, I just wanted to report back with a big thank you to both of you. I think my spa was built around Pump1. The larger pump would of encountered many issues during install. Everything went wrong, but in the end it all worked out. Took me about 8 hours including a trip to Home Depot to get a part that I broke during install. Spa is purring like a kitten! Thanks again and whatever you charge to replace pumps is not enough. What an ordeal for someone that has never done it before! 1 Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 27, 2020 Report Share Posted July 27, 2020 👍 1 Quote Link to comment Share on other sites More sharing options...