13jgolden Posted July 1, 2020 Report Share Posted July 1, 2020 Hello everyone, I am having issues with a Tiger River Spa Model Bengal MM. I recently hooked the spa up today to the electrical system and I keep tripping my 20 amp gfci breaker. The 30 amp gfci is operating correctly. The breaker instantly trips. I have a brand new ozone system, brand new 2 speed 230v pump, and a brand new heater relay board. When I unhook the wires from the the relay board to the main board the breaker no longer trips. With everything "Ozone, Circulation Pump, Main 2 Speed Pump, Control Panel, ECT unhooked from the main board the gfci still trips! Any help would be greatly appreciated! Quote Link to comment Share on other sites More sharing options...
RDspaguy Posted July 1, 2020 Report Share Posted July 1, 2020 The white wire from the spa must connect to the neutral terminal on the 20 amp breaker, not the neutral bar in the panel. The white "pigtail" on the breaker goes to the neutral bar. Quote Link to comment Share on other sites More sharing options...
13jgolden Posted July 1, 2020 Author Report Share Posted July 1, 2020 Thank you!!! This is exactly what was wrong! You are the best! Quote Link to comment Share on other sites More sharing options...