Flo Error On 2000 Sundance Optima


whee

Recommended Posts

Hello,

Troubleshooting a “FLO” error on my Sundance Optima, Model year 2000.

  1. Replaced filter
  2. Replaced heater (due to leaks)

    1. Bypassed smart logic board per Sundance instructions

[*]Replaced hi-temp sensor due to error

[*]Replaced circulation pump with Laing 6000-125

  1. Wired pump to direct always hot 240 volt feed, since the normal pump circuit board connector is not getting power. Is this OK?
  2. Per instructions used the flow restrictor in the pump

If I turn on the 2 speed pump, I can see the flow switch engage and the pump will run and the heater will turn on.

I can see the circulation pump is running and it pushes the flow switch, but about 10 seconds after turning the hottub on I get the “FLO” error and it never recovers. The circulation pump keeps running, but can’t control the hottub.

The circulation pump doesn’t push the flow switch as strongly as the 2 speed pump. I’m thinking probably bad flow switch, or could it be the circulation pump is not pushing enough water? I tried running without the filter; same results. Thoughts?

Thanks in advance!

-Peter

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...