Sundance Palermo Heating Issues


riverwalker

Recommended Posts

Heat indicator comes on when main circuit breaker is reset. Heat rises a few degrees and then goes out. Everything else is working fine.

I have replaced circulating pump, removed main filter, removed flow sensor and connected the leads to bypass the sensor.

This hot tub is in a rental cabin and guests coming in tomorrow are going to be plenty disappointed if no hot tub.....

Link to comment
Share on other sites

Heat indicator comes on when main circuit breaker is reset. Heat rises a few degrees and then goes out. Everything else is working fine.

I have replaced circulating pump, removed main filter, removed flow sensor and connected the leads to bypass the sensor.

This hot tub is in a rental cabin and guests coming in tomorrow are going to be plenty disappointed if no hot tub.....

I take it there's no error code on your top side control panel? Or is the top side not digital?

If digital is the display showing the correct temperature?

Could be bad temp or hi-limit sensor. To confirm you can temporarily switch the wires around; make the hi-limit sensor the temp, and the temp sensor the hi-limit. If the spa works again, don't leave it like that though :)

Link to comment
Share on other sites

Heat indicator comes on when main circuit breaker is reset. Heat rises a few degrees and then goes out. Everything else is working fine.

I have replaced circulating pump, removed main filter, removed flow sensor and connected the leads to bypass the sensor.

This hot tub is in a rental cabin and guests coming in tomorrow are going to be plenty disappointed if no hot tub.....

I take it there's no error code on your top side control panel? Or is the top side not digital?

If digital is the display showing the correct temperature?

Could be bad temp or hi-limit sensor. To confirm you can temporarily switch the wires around; make the hi-limit sensor the temp, and the temp sensor the hi-limit. If the spa works again, don't leave it like that though :)

Link to comment
Share on other sites

Heat indicator comes on when main circuit breaker is reset. Heat rises a few degrees and then goes out. Everything else is working fine.

I have replaced circulating pump, removed main filter, removed flow sensor and connected the leads to bypass the sensor.

This hot tub is in a rental cabin and guests coming in tomorrow are going to be plenty disappointed if no hot tub.....

I take it there's no error code on your top side control panel? Or is the top side not digital?

If digital is the display showing the correct temperature?

Could be bad temp or hi-limit sensor. To confirm you can temporarily switch the wires around; make the hi-limit sensor the temp, and the temp sensor the hi-limit. If the spa works again, don't leave it like that though :)

Thanks for getting back.

Yes, no error messages - digital

I bleieve it is showing correct temperature

I will swap as you suggest and report back.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...


×
×
  • Create New...