Thank you PoolGuy and Bugman. I have shorted the lead to pressure switch and it fired right up. There was 28 v going into it but only 19 coming out. That's the good news. the bad news is while I was taking out the lead wires off, the switch broke and water started shooting out. But I guess I needed a new switch any way. Now I am looking for one online and they more expensive than I thought.
About the codes I were getting, the fenwal blinks once, meaning Air Flow problem but I do not have a blower! Anyway the fenwal was not getting 24v becuase of the bad pressure switch, and it works fine once it recieves 24v. I need to check if it still blinks when the valve fires up.
Would a pressure switch with 3.1 PSI minimum rating work even though the manual says to use a 2.0 PSI switch? Also the manual syas to put some 50 w oil in the copper tube of the switch. I assume this is needed to keep water away from the switch to prevent corrosion. Would 10-40 oil be OK?